We moved into our house a little over a year ago. It took me several months before trying my Hf station on a temporary Alpha 1 antenna. The first day I did, I blew 4 Arc Fault breakers in the main panel. It took me about 4 months to figure it out then a few days ago I got this info from a friend from the ARRL. This may also help some of you guys. The upshot was that I changed out 4 arc fault breakers replacing them with regular ones and the problems went away. Here's what the ARRL said about it. You might find this interesting. From today's ARRL newsletter Your League: ARRL Helps Manufacturer to Resolve Arc Fault Circuit Interrupter RFI Problems The ARRL Lab has worked with a manufacturer of arc fault circuit interrupter (AFCI) breakers to resolve complaints that Amateur Radio RF was causing certain breaker models to trip unnecessarily. Like the more common ground fault circuit interrupter (GFCI), the AFCI is a safety device. Primarily designed to detect problems that could result in a fire, AFCIs detect potentially hazardous arc faults that result from often unseen damage or poor connections in wiring and in extension cords and cord sets. "Several months ago we started receiving reports from amateurs that when they transmitted, their AFCI breakers were tripping," said Mike Gruber, W1MG, the ARRL Lab's EMC specialist. He noted that the issue has been a topic of online ham radio discussions as well as on homeowner sites; it seems that stray RF is not the only thing that can cause a "nuisance trip" of an AFCI. Gruber pointed out that the National Electrical Code (NEC) already requires AFCIs in some household circuits, but not all US jurisdictions have adopted the requirement. W1AW Station Manager Joe Carcia, NJ1Q, with the AFCI test stand. [Mike Gruber, W1MG, photo] Gruber said that as AFCIs became more common in new construction in the US, reports started coming in that AFCIs in the vicinity - not just in the radio amateur's home - would trip in the presence of RF from an Amateur Radio transmitter. While each manufacturer's design is proprietary, most AFCIs detect arcs by monitoring the shape of the alternating current waveform, changes in current levels, voltage irregularities, and the presence of high frequency emissions or "noise." The ARRL Lab dug into the problem. "Last summer we built a test fixture in which we could test any type of circuit breaker," Gruber said. It involved using W1AW as an RF source. Gruber said he bought one of "every AFCI that I could get my hands on," but when the Lab began testing them during W1AW transmissions, none of the devices tripped.. A ham in New Mexico who had reported AFCI problems sent some of his breakers to the ARRL Lab, "and those tripped when we tested them," Gruber said. The problematic breakers were certain models made by Eaton Corporation. "We already had an Eaton breaker, an older model, but it did not trip," he noted, adding that the breaker had a yellow button. The newer model, which had a white button, did trip in the presence of RF, however, even at power levels down to about 50 W on 17 meters. Gruber contacted Eaton, and two of the manufacturer's engineers visited ARRL Headquarters in August. "Eaton was extremely cooperative and eager to resolve this," Gruber recounted. "They spent the day with us, going over our test methods and took some of the problematic breakers back with them, eventually developing a modified version. "We have just finished testing the new version of the breaker, and it did not trip during W1AW transmissions and in other tests," Gruber reported. He said the new breaker is still in the queue for UL approval. Eaton Engineering Director Andy Foerster said arc fault detection is challenging, in part because so many common household devices - such as vacuum cleaners and power tools that use motors with brushes - create arcing. In information provided to ARRL Eaton engineer Lanson Relyea said that because AFCIs rely on HF emission detection to verify arcing, "any signal that conducts or radiates a signal within the detection band of the AFCI can cause interference and cause the device to trip without the presence of a true arcing condition." Eaton and ARRL agreed that when the manufacturer comes out with any new models of breakers, it will ask the League to test them at W1AW. "It's a win-win situation," Gruber said. Eaton also has agreed to work with anyone having a problem with RF tripping its AFCIs. Hams experiencing unwanted tripping problems with their or their neighbors' AFCIs should first contact the manufacturer. In the case of Eaton breakers, contact Bob Handickgg412-893-3746) or Joe Fello (412-893-3745). Read more.